jfelix
Member


Joined: Saturday December 31st, 2005
Location: Dallas, Georgia USA
Posts: 814
Picture: [Download]
Status:  Offline
 Posted: Thursday April 10th, 2008 01:00 am
QuoteReply
I am wanting to convert a 30amp wwo line to 2 seperate 110 lines. But here is the thing, I need it to use it as 220 in the summer. Here is the deal. I have a pump that I use to draw water from our creek for irrigating the lawn. In teh winter (OCt.) we shut it down becuase we do not need it. So I have the power just setting there at Christmas just screaming USE ME!

So what would be the easiest way to assign this thing double dity. Right now it has a breaker and the main and a shut off box at the pump so I can open the panel and pull the power if ned be. I wanted to wire it when we installed it, but my father-in-law lacked the know-how on setting it up and a 110 plug.



____________________
Joey Felix

http://www.att.net/p/PWP-felixfamilylights




Back To Top QuoteReply

Santas Helper
Member


Joined: Tuesday December 20th, 2005
Location: Oklahoma City, Oklahoma USA
Posts: 2265
Picture: 
Status:  Offline
 Posted: Thursday April 10th, 2008 02:08 am
QuoteReply
Joey,

With 220, you have 2 hots coming off the breaker with a ground and a neutral for the pump (should be 4 wires). With caution on any electrical stuff, disconnect the wires going to the pump and add your 2 seperate 110 hots to it. So you should have 1 hot, ground and neutral for each line (6 wires total).

Please make sure you exerise caution with electrical. Make sure power to the box is OFF before doing anything. And if your still not sure, get some help.

Tom



____________________
Tom (aka Santa's Helper)
http://www.bricktownamusement.com

Back To Top QuoteReply

dougd
Member


Joined: Tuesday October 10th, 2006
Location: Cleveland, Tennessee USA
Posts: 101
Picture: [Download]
Status:  Offline
 Posted: Thursday April 10th, 2008 02:50 am
QuoteReply
I have a question along this line. Lets say the 220 breaker is rated at 30 amps. If you use each leg and end up with 2 110 circuits will the circuits kick at 30 amps? Hope that makes sense. The reason for the question is I have several 220 volt 30 amp breakers and was wondering if I could make use of them. Thanks.

Back To Top QuoteReply

jfelix
Member


Joined: Saturday December 31st, 2005
Location: Dallas, Georgia USA
Posts: 814
Picture: [Download]
Status:  Offline
 Posted: Thursday April 10th, 2008 05:58 am
QuoteReply
Santas Helper wrote: Joey,

With 220, you have 2 hots coming off the breaker with a ground and a neutral for the pump (should be 4 wires). With caution on any electrical stuff, disconnect the wires going to the pump and add your 2 separate 110 hots to it. So you should have 1 hot, ground and neutral for each line (6 wires total).

Please make sure you exercise caution with electrical. Make sure power to the box is OFF before doing anything. And if your still not sure, get some help.

Tom


If I understand what your saying I would need to disconnect the pump totally and reconnect it after Christmas, right? I would like to keep it connected if I can. This is my thought, would this work.

Split up the two hots to go to 2 separate outlets, then run the neutral to both outlets, and the grounds. I was thinking of splitting up everything in a junction box. Then from each outlet run the hots to the pump with one of the neutrals and one grounds going to the pump as well. Does this make sense?

 

As for the above question: I believe that your double thirty pole breaker would make  60 amps at 110. I am not an electrician so my opinion is strictly that, an opinion. That being said you must also consider you are sharing the ground and neutral on that circuit. Also, it is never recommended to use more than 80% of your amps on a breaker.



____________________
Joey Felix

http://www.att.net/p/PWP-felixfamilylights




Back To Top QuoteReply

TED
Member


Joined: Monday November 28th, 2005
Location: Little Rock, Arkansas USA
Posts: 4929
Picture: 
Status:  Offline
 Posted: Thursday April 10th, 2008 07:15 am
QuoteReply
dougd wrote: I have a question along this line. Lets say the 220 breaker is rated at 30 amps. If you use each leg and end up with 2 110 circuits will the circuits kick at 30 amps? Hope that makes sense. The reason for the question is I have several 220 volt 30 amp breakers and was wondering if I could make use of them. Thanks.
  In a 220 (240) volt service you actually have two hot 120 volt feeds coming in.  In order to get 220 you use both hots.  What you are calling a "220 breaker" is really a double pole breaker which consists of 2 30 volt breakers one for each 120 feed.  So the answer is yes if either 120 feed draws over 30 amps it will trip the breaker.

                                                                    TED

Back To Top QuoteReply

dtedebear
Member


Joined: Monday December 3rd, 2007
Location: Olympia, Washington USA
Posts: 7
Picture: 
Status:  Offline
 Posted: Thursday April 10th, 2008 08:34 am
QuoteReply
The simplist solution would be to add two 20 AMP circuit breakers to the main panel for your two new circuits.  You could leave everything 'on' but only use the pump OR the Christmas lights but not both at the same time.

If you do not have room in the main panel, the next easiest solution is to add a sub-panel.  Use the current double 30 AMP circuit breaker in the main panel to feed the sub-panel.  In the sub-panel have:
  • a 30 AMP double breaker (220 V) for the pump.  Move the pump wires from the main panel to this sub-panel.
  • four 15 AMP (or two 20 AMP) single circuit breakers (110 V) for your light display. 
This will allow you to power the pump and/or the Christmas lights with the flick of a switch (circuit breaker), but don't use both at the same time.  If you draw more than 30 AMPs per phase you will pop the circuit breaker in the main panel.  Make sure the you have the 15 or 20 AMP breakers split evenly on the two phases coming in to the sub-panel.

I would not pull power from the Pump Switch for your Christmas light circuits.  Call an electrician to help you with this.



____________________
DanS
Back To Top QuoteReply

Tony Furst



Joined: Tuesday December 4th, 2007
Location: Grove City, Ohio USA
Posts: 224
Picture: [Download]
Status:  Offline
 Posted: Thursday April 10th, 2008 09:16 am
QuoteReply
You can't use the pump breaker for your lights quite the way you have envisioned.  The easiest setup is to install a double pole double throw disconnect adjacent to your breaker panel.  This will provide you with a code approved method of having one source of power feed two different loads.  This prevents someone from accidentally turnig the power on to the pump and the receptacles at the same time.  Also remember to use GFCI receptacles outdoors.

 

Tony



____________________
Do not meddle in the affairs of dragons, for you are crunchy and taste good with ketchup.

Back To Top QuoteReply

Toymakr000
Member


Joined: Wednesday January 18th, 2006
Location: Livonia, Michigan USA
Posts: 1512
Picture: [Download]
Status:  Offline
 Posted: Thursday April 10th, 2008 12:07 pm
QuoteReply
My first thought was to use a 220 receptical/plug for you pump then make a plug in sub panel for Christmas. That way you can swap the tow without having both plugged in simultaneously. Make sure it 's 4 wire......



____________________
Gary Slater

Back To Top QuoteReply

Tony Furst



Joined: Tuesday December 4th, 2007
Location: Grove City, Ohio USA
Posts: 224
Picture: [Download]
Status:  Offline
 Posted: Thursday April 10th, 2008 12:58 pm
QuoteReply
Gary,

I like that idea as well, I wasn't fully functional this morning when I posted my comment about the DPDT disconnect.

Tony



____________________
Do not meddle in the affairs of dragons, for you are crunchy and taste good with ketchup.

Back To Top QuoteReply

gymnasium
Member


Joined: Friday December 7th, 2007
Location: Kennesaw, Georgia USA
Posts: 153
Picture: 
Status:  Offline
 Posted: Thursday April 10th, 2008 02:32 pm
QuoteReply
Joey, I am doing something similar, but wanting to use my A/C power allocation for lights in the winter.  The simplest solution for me is to pull two 12ga wires from my panel to an outside box which coincidentally will by right next to the outside A/C unit and put two 20amp GFCI outlets in that box.  In the summer I will just turn the breakers off for the Christmas light outlets and in the winter turn off the A/C breaker as I already do now.  Fortunately the panel is not to far from where the outside outlets will go, the wires will be easy to pull, and the box has plenty of spare breaker room.  I already have all the materials, just need to get my vinyl siding cut and a mounting block inserted.

Does this mean you are not going to sell the house?



____________________

Jim Nealand
Back To Top QuoteReply

jfelix
Member


Joined: Saturday December 31st, 2005
Location: Dallas, Georgia USA
Posts: 814
Picture: [Download]
Status:  Offline
 Posted: Thursday April 10th, 2008 03:27 pm
QuoteReply
I am thinking my best bets are 220 plugs and a sub or installing some sort of panel at the pump. I already have a disconnect down there, but a small sub might be better. Like I said I just hate having this power sitting idlein winter. I have a 100amp sub out back, but this is across the uard (about 150+ft from the house. So it would be nice to not run more power.

Jim to answer your question, we still plan to put the house up sometime in the future, just not sure how "near" that future is.



____________________
Joey Felix

http://www.att.net/p/PWP-felixfamilylights




Back To Top QuoteReply

AI
Member
 

Joined: Saturday November 25th, 2006
Location: Allentown, Pennsylvania USA
Posts: 838
Picture: 
Status:  Offline
 Posted: Saturday April 12th, 2008 01:41 am
QuoteReply
Just remember the pump doesn't need a neutral so its probably not there and you will have to run new wire to include one. You can not put a 110v outlet on a 30 amp breaker, the most they are rated for is 20 amps so you will need additional breakers.

Probably not going to be as easy as you hoped. Sorry AI



____________________
Back To Top QuoteReply

dwp49423
Member


Joined: Monday December 5th, 2005
Location: Holland, Michigan USA
Posts: 116
Picture: 
Status:  Offline
 Posted: Saturday April 12th, 2008 03:15 am
QuoteReply
AI wrote: Just remember the pump doesn't need a neutral so its probably not there and you will have to run new wire to include one. You can not put a 110v outlet on a 30 amp breaker, the most they are rated for is 20 amps so you will need additional breakers.

Probably not going to be as easy as you hoped. Sorry AI
Technically there are 30amp 110v circuits though they are highly specialized.  Look at campgrounds and marinas.    The RV hookup poles are either 110v 30amp (3 Prong) or 220 50amp (4 Prong).  Probably a way somehow to use these if you know how an RV, travel trailer or boat is wired.



____________________
-Dave
It's "Merry Christmas" not "Happy Holidays"
Back To Top QuoteReply

mnkyboy
Member


Joined: Tuesday December 11th, 2007
Location: Glendale, Arizona USA
Posts: 78
Picture: [Download]
Status:  Offline
 Posted: Saturday April 12th, 2008 09:02 am
QuoteReply
dwp49423 wrote:
Technically there are 30amp 110v circuits though they are highly specialized.  Look at campgrounds and marinas.    The RV hookup poles are either 110v 30amp (3 Prong) or 220 50amp (4 Prong).  Probably a way somehow to use these if you know how an RV, travel trailer or boat is wired.



you mean connections like this!

1 50 amp 240v 4 prong RV plug (available at home depot or Lowes for 30 bucks)

1 36ft 50 amp 6/3,8/1 cable  with 50 rv plug on one end and a Marinco 50 amp twistlock on the other

1 CEP spider box with 6 120v 20amp GFCI's

6 20 amp twistlock triple taps

Attachment: spiderbox2.JPG (Downloaded 73 times)

Last edited on Saturday April 12th, 2008 09:07 am by mnkyboy



____________________

http://griswaldsrus.spaces.live.com/
Back To Top QuoteReply

AI
Member
 

Joined: Saturday November 25th, 2006
Location: Allentown, Pennsylvania USA
Posts: 838
Picture: 
Status:  Offline
 Posted: Sunday April 13th, 2008 11:36 am
QuoteReply
jfelix wrote: I am wanting to convert a 30amp wwo line to 2 seperate 110 lines. But here is the thing, I need it to use it as 220 in the summer. Here is the deal. I have a pump that I use to draw water from our creek for irrigating the lawn. In teh winter (OCt.) we shut it down becuase we do not need it. So I have the power just setting there at Christmas just screaming USE ME!

So what would be the easiest way to assign this thing double dity. Right now it has a breaker and the main and a shut off box at the pump so I can open the panel and pull the power if ned be. I wanted to wire it when we installed it, but my father-in-law lacked the know-how on setting it up and a 110 plug.

OK If you have the proper neutral return line then put a sup panel out at the pump. With one 30 amp 220 volt breaker for the pump and 4 15 amp 110 volt breakers that go to outlets. AI



____________________
Back To Top QuoteReply

Tony Furst



Joined: Tuesday December 4th, 2007
Location: Grove City, Ohio USA
Posts: 224
Picture: [Download]
Status:  Offline
 Posted: Sunday April 13th, 2008 01:30 pm
QuoteReply
As stated before the problem with this configuration is that it does not prevent a serious overload condition of the breaker that feeds the sub panel. 

If the existing 30A breaker at the main panel feeds the subpanel and both the receptacles and pump are powered at the same time then the 30A breaker at the main could be overloaded. 

While I realize that with the intent being that this would only be utilized at Christmas you have to remember that at some point in time the house may be owned by someone else or someone may try and utilize one or all of those receptacles while the pump is operating.

The best and safest method is to use either a DPDT disconnect that allows either the subpanel or the pump to be powered at one time but not both, or have the breaker feed a cordset and then the cordset can be plugged into the subpanel or the feed to the pump.

The intent here is to make sure that the installation is safe at all times and cannot be operated either intentionally or unintentionally at a current greater than which it was designed to handle.

Tony



____________________
Do not meddle in the affairs of dragons, for you are crunchy and taste good with ketchup.

Back To Top QuoteReply

AI
Member
 

Joined: Saturday November 25th, 2006
Location: Allentown, Pennsylvania USA
Posts: 838
Picture: 
Status:  Offline
 Posted: Sunday April 13th, 2008 02:38 pm
QuoteReply
As stated before the problem with this configuration is that it does not prevent a serious overload condition of the breaker that feeds the sub panel. 

If the existing 30A breaker at the main panel feeds the subpanel and both the receptacles and pump are powered at the same time then the 30A breaker at the main could be overloaded. 
and then what would happen? AI



____________________
Back To Top QuoteReply

Tony Furst



Joined: Tuesday December 4th, 2007
Location: Grove City, Ohio USA
Posts: 224
Picture: [Download]
Status:  Offline
 Posted: Sunday April 13th, 2008 04:27 pm
QuoteReply
Assuming that the 30A breaker works as intended then the breaker trips and everything goes off.  Worst case is that the breaker fails and causes a fire.  In either case not exactly the planned outcome. 

Why would you intentionally create a potential serious overload condition? 

I haven't researched the NEC as of yet on this particular installation method but I am quite sure if I review all of the different sections of the code relating to motor control and motors adjacent to water there are probably a few different code sections that may also prevent doing this.

Tony



____________________
Do not meddle in the affairs of dragons, for you are crunchy and taste good with ketchup.

Back To Top QuoteReply

jfelix
Member


Joined: Saturday December 31st, 2005
Location: Dallas, Georgia USA
Posts: 814
Picture: [Download]
Status:  Offline
 Posted: Sunday April 13th, 2008 06:43 pm
QuoteReply
This is all good information to know wile I am planning this out. I am planning on making any changes oer the summer.

If I were to stay here for my lifetime than I would not worry about the pump and  outlets being on at the same time, because I know enough to never do that. But I can see where Tony is  coming from. We do not plan to stay here so I do need to make certain it is done right.

 



____________________
Joey Felix

http://www.att.net/p/PWP-felixfamilylights




Back To Top QuoteReply

AI
Member
 

Joined: Saturday November 25th, 2006
Location: Allentown, Pennsylvania USA
Posts: 838
Picture: 
Status:  Offline
 Posted: Sunday April 13th, 2008 08:06 pm
QuoteReply
You can use Hubble twist lock plugs. A female after the shutoff and a male on the pump. Then set up a sub-panel with a male end that has breakers and GFIs. In the winter unplug the pump and plug in the sub-panel.:smile: AI



____________________
Back To Top QuoteReply